one for the sparkies...
so I wondering if I should try and get away with a 6mm T&E over a 10mm T&E.

fitting new cooker rated at 14.8kW but I suspect that is full tilt with no diversity.
cooker installation says 46A MCB but I'm thinking of going with 40A and a 6mm cable as I don't envisage every having everything going full whack all at the same time.?

thoughts please Mr. Green
Post #1018692 18th Dec 2023 7:02pm
View user's profile Send private message View poster's gallery Reply with quote
lohr500



Member Since: 14 Sep 2014
Location: Skipton
Posts: 1317

United Kingdom 2013 Defender 110 Puma 2.2 XS CSW Santorini Black
Daft question Caterham as I have no knowledge in this area, but why wouldn't you follow the recommended installation requirements?
Is the cost of the higher rated cable and MCB significant in the scale of things?
Post #1018695 18th Dec 2023 7:23pm
View user's profile Send private message View poster's gallery Reply with quote
Caterham



Member Since: 06 Nov 2008
Location: Birmingham
Posts: 6300

England 2011 Defender 110 Puma 2.4 XS CSW Stornoway Grey
lohr500 - the cost might not be significant but the pain in the rear is when it comes to installing.
I'm fully appreciate why you've responded as you have but I'm inclined to think the manufacturers suggestion is a 'cover ones rear' approach.
As noted I can't imagine for one second I'll have two ovens, a grill and all 5 or 6 hobs going all at once and all on max so I don't really see the point of catering for that scenario and hence the question.

in the word of electrics / design it is quite normal to apply diversity - and thats effectively what I'm doing (I think Very Happy ).

valued feedback all the same. Thumbs Up
Post #1018696 18th Dec 2023 7:28pm
View user's profile Send private message View poster's gallery Reply with quote
diesel_jim



Member Since: 13 Oct 2008
Location: hiding
Posts: 6093

United Kingdom 2006 Defender 110 Td5 SW Epsom Green
Go with the higher rating. As a sparky myself (albiet more data/CCTV/door entry stuff, but also 18th and part P certified) go with the bigger size..

"you never know"

Quickly looking at TLC... for 10m of 6mm T&E or 10mm T&E...



Click image to enlarge



Not much in it..
Post #1018697 18th Dec 2023 7:32pm
View user's profile Send private message View poster's gallery Reply with quote
diesel_jim



Member Since: 13 Oct 2008
Location: hiding
Posts: 6093

United Kingdom 2006 Defender 110 Td5 SW Epsom Green
Diversity usually applies to a whole building, as in, not all of the lights and heaters are on at the same time.

An oven? not sure, but it wouldn't take much say on a christmas day to have everything going at once.
Post #1018698 18th Dec 2023 7:34pm
View user's profile Send private message View poster's gallery Reply with quote
300TDi CSW Phil



Member Since: 03 Apr 2016
Location: Bracknell
Posts: 750

United Kingdom 1995 Defender 110 300 Tdi CSW Epsom Green
Domestic ovens are the only thing in a house where diversity is applied.
To size the cable and breaker take 10A as a given and then 30% of the rest of the rated max. 1995 300 Tdi Epsom Green - It's a keeper.
Wide Track Sankey- In bits- Gone to a new home
M0XQS
Post #1018707 18th Dec 2023 8:44pm
View user's profile Send private message View poster's gallery Reply with quote
windy81



Member Since: 14 Mar 2018
Location: North Wales
Posts: 311

Wales 1992 Defender 90 200 Tdi HT Firenze Red
Size the MCB with the cable rating.

The MCB/RCBO is to protect the cable and not the appliance so if you want to use 6mm with a 40a MCB that's fine, but don't be surprised if it trips if you have the oven on full tilt.
Post #1018731 19th Dec 2023 2:32pm
View user's profile Send private message View poster's gallery Reply with quote
Procta



Member Since: 03 Dec 2016
Location: Sunderland
Posts: 5183

United Kingdom 
When me and my dad did the wash house hot water system, we used the heater system off a electric shower, I bought the thicker wire for it, and the stated MCB, just so there was no foul ups. Also when we added more sockets into the wash house we bumped the MCB to next size, even though we wont have all the sockets going at once etc. Defender TD5 90 ---/--- Peugeot 306 HDI hatch back

Success is 90% Inspiration and 4 minutes Preparation # you can make it!
Post #1018736 19th Dec 2023 3:19pm
View user's profile Send private message View poster's gallery Reply with quote
Co1



Member Since: 19 Aug 2018
Location: North Yorkshire
Posts: 3679

United Kingdom 2013 Defender 90 Puma 2.2 HT Loire Blue
What’s the length of the cable run? Send me the details and I’ll work it out for you in the morning. You’ve also got volt drop to consider if the length is considerable, so while 6mm may be ok for the load with diversity applied, it might be no good with volt drop.

Procta: bumping your MCB to the next size because you added more sockets isn’t a good idea. The MCB is there to protect the cable, not the sockets or appliances. You’ve actually increased the risk of fire by doing that so I would recommend installing and correctly rated MCB.
Post #1018764 19th Dec 2023 7:04pm
View user's profile Send private message View poster's gallery Reply with quote
Screbble



Member Since: 26 Apr 2015
Location: Lancashire
Posts: 2106

United Kingdom 2004 Defender 90 Td5 XS CSW Zambezi Silver
Post #1018767 19th Dec 2023 7:16pm
View user's profile Send private message View poster's gallery Reply with quote
Procta



Member Since: 03 Dec 2016
Location: Sunderland
Posts: 5183

United Kingdom 
Co1 wrote:
What’s the length of the cable run? Send me the details and I’ll work it out for you in the morning. You’ve also got volt drop to consider if the length is considerable, so while 6mm may be ok for the load with diversity applied, it might be no good with volt drop.

Procta: bumping your MCB to the next size because you added more sockets isn’t a good idea. The MCB is there to protect the cable, not the sockets or appliances. You’ve actually increased the risk of fire by doing that so I would recommend installing and correctly rated MCB.


yeah, you are supposed to do a ring main, like a return feed if am right? not sure how me and my dad will do that, where our end socket is, Which is outside one at the front of the house. Defender TD5 90 ---/--- Peugeot 306 HDI hatch back

Success is 90% Inspiration and 4 minutes Preparation # you can make it!
Post #1018769 19th Dec 2023 7:35pm
View user's profile Send private message View poster's gallery Reply with quote
Screbble



Member Since: 26 Apr 2015
Location: Lancashire
Posts: 2106

United Kingdom 2004 Defender 90 Td5 XS CSW Zambezi Silver
Procta, you should get that wiring checked by a spark as just reading it it makes me concerned. As said above you need the MCB to protect the cable otherwise it’s dangerous. You can have a radial instead of a ring but again you’ll need an appropriately rated (lower) MCB. You also need to ensure your earthing is spot on, and I’m not sure how you’d do that without an earth loop impedance test. Better safe than sorry 👍
Post #1018770 19th Dec 2023 7:43pm
View user's profile Send private message View poster's gallery Reply with quote
Caterham



Member Since: 06 Nov 2008
Location: Birmingham
Posts: 6300

England 2011 Defender 110 Puma 2.4 XS CSW Stornoway Grey
thank you guys.
I was up against it have bought a drum of 10mm......
but reading some of the posts I'm very inclined to swap it out for 6mm Smile
we're just perhaps 9m for the fuse board - I'm allowing another 1.5m for the 'fly lead' from DP switch to the over itself - so no major volt drops to be concerned about.

from memory (which isn't the best) I'm expecting to break at least the odd one or two plastic surface patresses while terminating the cable into the switch and hence why I'm keen to go with the smaller cable? Thumbs Up
Post #1018802 20th Dec 2023 9:28am
View user's profile Send private message View poster's gallery Reply with quote
Co1



Member Since: 19 Aug 2018
Location: North Yorkshire
Posts: 3679

United Kingdom 2013 Defender 90 Puma 2.2 HT Loire Blue
Full load at 14.8 kw gives 64.35A max demand. To get it down to a 46A MCB means diversity of 70% ish. Is that reasonable? Volt drop on that length will be 4.09V using 6mm so absolutely fine (max allowable of 11.5V).
Post #1018805 20th Dec 2023 10:21am
View user's profile Send private message View poster's gallery Reply with quote
Procta



Member Since: 03 Dec 2016
Location: Sunderland
Posts: 5183

United Kingdom 
Screbble wrote:
Procta, you should get that wiring checked by a spark as just reading it it makes me concerned. As said above you need the MCB to protect the cable otherwise it’s dangerous. You can have a radial instead of a ring but again you’ll need an appropriately rated (lower) MCB. You also need to ensure your earthing is spot on, and I’m not sure how you’d do that without an earth loop impedance test. Better safe than sorry 👍


i will look at MCB again, we still have the old one about anyway, We are looking at getting a compressor next year, which is on a trip system at the socket end, i fitted four of these, two for outside and two in side, one for the compressor and the other was the one they always used for extensions. My dad has fitted a little switch box thing with a light on, which you are supposed to do, every so many?? which because they had a freezer in there, a while ago before me and my dad decided to kit things out. ( just to give him something to do, as he has retired) Thumbs Up Defender TD5 90 ---/--- Peugeot 306 HDI hatch back

Success is 90% Inspiration and 4 minutes Preparation # you can make it!
Post #1019044 23rd Dec 2023 2:13am
View user's profile Send private message View poster's gallery Reply with quote
Post Reply  Back to top
Page 1 of 2 12>
All times are GMT

Jump to  
Previous Topic | Next Topic >
Posting Rules
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum



Site Copyright © 2006-2024 Futuranet Ltd & Martin Lewis
DEFENDER2.NET RSS Feed - All Forums