This can't be repeated often enough! I hear that misunderstanding a lot!
windy81 wrote:Size the MCB with the cable rating
The MCB/RCBO is to protect the cable and not the appliance
Co1 wrote:Bumping your MCB to the next size because you added more sockets isn’t a good idea. The MCB is there to protect the cable, not the sockets or appliances. You’ve actually increased the risk of fire by doing that so I would recommend installing and correctly rated MCB.
Screbble wrote:As said above you need the MCB to protect the cable otherwise it’s dangerous.
|
23rd Dec 2023 3:23pm |
|