Home > Off Topic > one for the pipe welders out there
Page 2 of 2 <12
RFT
United Kingdom 2010 Defender 130 Puma 2.4 HCPU Zermatt Silver
Re the question ref Pressure Vessel Regulations.
As I assume you are modifying an existing system, if so you need to be compliant with the Pressure System Safety Regulations
https://www.hse.gov.uk/pressure-systems/pssr.htm
And for the design and supply of a new system the pressure system (safety) regulations will apply.
https://www.legislation.gov.uk/uksi/2016/1105/contents
Needless to say these impose very complex controls on high pressure and high hazard systems (my world is oil & gas) but for lower pressure, small volume, low hazard fluids the controls tend to rely on “sound engineering practice” often covered by training and competence, as such it is alway best to use skilled and competent installers using conventional and proven technology. 130 Puma HCPU with an Artica 240LR Demountable Camper
Post #962062 17th Aug 2022 10:05pm
Caterham
thank you very much. not read all of the HSE / ACOP but suspect the following is what is most relevant;
Any repair or modification (including extensions or additions) should be
designed in accordance with appropriate standards, taking into account the
expected future duty of the system as well as the original design
specification. It should be done by a person competent to do such work.
business and usual then Thumbs Up
thank you.
Post #962085 18th Aug 2022 7:33am
Caterham
curious to see if anyone is as surprised as I was when I saw this install.
those familiar with unvented domestic hot water systems - anything in the photo that surprises you?
note these are calorifiers and not direct / gas fired heaters. probably obvious considering the plate heater exchangers.
Post #962149 18th Aug 2022 4:52pm
bear100
Maybe just the picture but the PRV’s look big on the cylinders? Other than that, twin plate to plate, twin booster sets etc, I presume the plant is hydraulically separated from the rest the system to preserve the boilers? ie dirty or old system. 2023 Defender L663 V8
2010 110 XS Utility 2.4TDCI
1993 110 csw 200 tdi (gone)
1994 90 HT 300 tdi (gone)
1994 discovery 300tdi (gone)
90 hybrid 3.5 v8 (gone)
Post #962156 18th Aug 2022 5:43pm
Caterham
yep that was exactly my thought - they look rather large.
not only that with the plate heat exchanger is it even possible for the system to overheat?
if not then I presume there are way too may PRV's?
there are further PRV's behind the cylinders too Confused
I guess better too many than too few?
until someone has to pay to replace them all Mr. Green
the plate heat exchangers aren't there to separate the boilers from an old system - the whole install was new?
Post #962159 18th Aug 2022 5:47pm
bear100
A typical plate to plate will only loose around 3/5c heat loss across them, the combined temperature and pressure relief size on the cylinder will be determined by the cylinder manufacturer, cylinders are also made to measure with specified tappings, maybe the installer didn’t realise and fitted a large PRV instead of bushing down? As long as they are sized right few the better really from a maintenance point of view and cost to repair or replace if they pass which they do.
Seems an awful big expense to fit PTP’s on a new traditional system? 2023 Defender L663 V8
Post #962176 18th Aug 2022 7:46pm
Daisy90
United Kingdom 2001 Defender 90 Td5 SW Alveston Red
Can it not be rotated enough in situ to get a weld completed ?
Post #962177 18th Aug 2022 7:46pm
Caterham
thank you for the thoughts but unfortunately that's not an option.
just to give you some background.
we have some basement boilers serving ground floor retail with offices above.
the retail requires heating both for extended periods during the week and weekend. if we can install a 3 port by-pass then we can effectively drop a couple of hundred radiators out of the circuit. Mr. Green Thumbs Up
Post #962992 26th Aug 2022 4:07pm
Caterham
anyone familiar with costs.
another property - we're looking to run a new flow and return up a building. will be 65mm increasing to 100mm but if we assume 100mm and circa 3.5 mtrs per floor (ie worst case).
was initially looking at running copper mapress for speed etc but costs are mega so I'm now inclined to think heavy steel with Megapress couplers / fittings (35mm connections f&r per floor) might be the best option.
costs appear to have gone through the roof recently.
anyone familiar with current prices and could suggest a budget cost for installing heavy steel 100mm x2 (f&r) on a per floor basis (would include brakets and lagging) - just approx. Thumbs Up
oh - and any interested in pricing the works - would be Midlands area.
Post #964100 5th Sep 2022 4:48pm
Page 2 of 2 <12