Home > Off Topic > 3 phase mains question
excossack
We have 3 phase UPS's at work in a new server room
Each UPS splits off to DB each with 8 breakers output at 230v
Trying to work out a rough loading figure in Watts - I can see the the L1/L2/L3 loads at the UPS but not the watts
The online calc I have used offers:
AC single phase
AC 3 phase Line 2 Line
AC 3 phase Line to neutral
as options.
Doing the calc with each option gives different readings
How can you tell what you have L2L or L2N ? 1999 Defender TD5 110
Regards
John M0VAZ
Econet Station 48 no clock
Post #994126 26th May 2023 1:33pm
TexasRover
I recall i learned that in Europa the single phase voltage of 230v is between line and neutral. Between lines it's 400v
How does the UPS display the load? In Amps?
Post #994145 26th May 2023 5:11pm
Co1
Re: 3 phase mains question
AC single phase
as options.
What info have you got at the UPS, Amps? You’ve got 230V per phase, so multiply that by the load in Amps of that phase and that will give you wattage per phase.
Post #994150 26th May 2023 5:34pm
excossack
Yea I have info in amps on the UPS which I can work out to Watts but an on line calculator also mentioned power factors and option to choose AC single or AC 3 phase and then options for L2L or L2N
The amount of Watts consumed varies depending on single or L2L etc.
I worked through all options and took each result so I have a range of Watts to choose from
We have the sparks due in next week to clamp test each output so we can get a reading to better understand the server racks that are consuming the most so we can try to re-balance the outputs.
L1 - 75%
L2 - 62%
L3 - 3%
We know L3 is under used at the mo so we need to work out which kit to move etc 1999 Defender TD5 110
Regards
John M0VAZ
Post #994162 26th May 2023 7:22pm